RainbowFS
Mechanical
- Apr 12, 2010
- 33
Trying to be brief, I'm involved in a hospital remodel that has two dry 6" standpipes (circa 1972) about 200 ft. apart. The remodel means that the FDC of one of them is going away. It was decided to interconnect the standpipes across the 4th floor roof to fix the problem.
The original hospital retained engineer declined to handle the project at the last minute and this got dropped in my lap.
I thought that running a six inch line across the roof would be the logical approach, but the fire marshal wants calcs.
I have a sprinkler calc program, two actually. (Sigma7700, 8800) So I've been trying to fill the slots in that program to get a workable equation, but it just isn't coming out.
So- the info I do have is:
The standpipe rises 55 ft. from FDC(5" Storz) to the high point, then about 220 ft. over to the top of the other one.
The AHJ gave me some fire truck info, their smallest pump truck: this is what I got
1000 gpm @ 150 psi.
700 " @ 200 "
500 " @ 250
City water flow from a near by hydrant is
Stat- 68.5
Res - 61, flowing 10,000 gpm
I'm told I need to flow 750 gpm (three points, highest, most remote, and one in the primary riser, I think)
Filling the formulae is the where the problem is, I hope.
Is the K-factor of a 2 1/2" valve flowing 250 gpm @ 100 psi, 10?
I am familiar with my sprinkler calc program, but applying it to this situation has my stumped.
My eternal thanks to any insight here.