Hi Guys,
I'm doing some simulations on software CYMGRD for earth substation, and i am really need some light on that..
Informations to do mesh:
BUS 138kV - ICC = 7kA - Remote contribuition 100%
BUS 13.8kV - ICC = 12kA - Remote contribuition 0% (dont have neutrals).
In my country they don't use neutrals on feeders..So i made simulations based on this.
I attach a picture to understand parameters.
My doubts:
1) When i change remote contribuition in BUS 13,8kV to 60% the software make calculations based on 12kA. But below 60% (0% at 59%) software does simulations based on 7kA (BUS 138kV), why?
2) Why software consider ICC 7kA and not 12kA? I understand that a 12kA LG fault is worse that 7kA.
i know there is a SF and DF (split factor and decrement factor) but i cant understand why 7kA are consider for calculations and not 12kA...
Can anyone shed some light on it
Thanks for your time...
DOWNLOAD PICTURE FILE -->
I'm doing some simulations on software CYMGRD for earth substation, and i am really need some light on that..
Informations to do mesh:
BUS 138kV - ICC = 7kA - Remote contribuition 100%
BUS 13.8kV - ICC = 12kA - Remote contribuition 0% (dont have neutrals).
In my country they don't use neutrals on feeders..So i made simulations based on this.
I attach a picture to understand parameters.
My doubts:
1) When i change remote contribuition in BUS 13,8kV to 60% the software make calculations based on 12kA. But below 60% (0% at 59%) software does simulations based on 7kA (BUS 138kV), why?
2) Why software consider ICC 7kA and not 12kA? I understand that a 12kA LG fault is worse that 7kA.
i know there is a SF and DF (split factor and decrement factor) but i cant understand why 7kA are consider for calculations and not 12kA...
Can anyone shed some light on it
Thanks for your time...