I submitted this post in "Electric Motors & Controlls" but wanted to make sure I submitted it in the right catagory.
I work for a utility company and a customer of ours requested a 3-phase padmount 480V delta transformer to connect a 3-phase 480V pump motor. These are rare and it is unfeasible for us to stock, so we decided to provide them with a 3-phase 480Y/277V connection.
Has anyone experienced any problems with connecting a 3-phase 480 volt delta motor w. a 3-phase 480Y/277V xfmr? The motor has a soft start and a breaker to protect from motor faults (phase imbalance). The motor is getting 480 volts per phase. The equipment is grounded for safety. It doesn't seem to me to be a problem.
Our customer brought up the idea that a phase imbalance on the primary transformer side will cause the motor to burn up, where as with a delta transformer this wouldn't happen. It seems to me that a phase imbalance would affect them whether it is a delta or a wye connection, i.e., the delta voltage is equal to the load times the difference of two phase of the transformer primary (Vdelta = Z x (Ia - Ib)), so that if one primary phase has low voltage it will still cause an imbalance on the motor. The breaker and motor protection will protect them and us either way.
Am I thinking correctly? Suggestions? Thank you much.
I work for a utility company and a customer of ours requested a 3-phase padmount 480V delta transformer to connect a 3-phase 480V pump motor. These are rare and it is unfeasible for us to stock, so we decided to provide them with a 3-phase 480Y/277V connection.
Has anyone experienced any problems with connecting a 3-phase 480 volt delta motor w. a 3-phase 480Y/277V xfmr? The motor has a soft start and a breaker to protect from motor faults (phase imbalance). The motor is getting 480 volts per phase. The equipment is grounded for safety. It doesn't seem to me to be a problem.
Our customer brought up the idea that a phase imbalance on the primary transformer side will cause the motor to burn up, where as with a delta transformer this wouldn't happen. It seems to me that a phase imbalance would affect them whether it is a delta or a wye connection, i.e., the delta voltage is equal to the load times the difference of two phase of the transformer primary (Vdelta = Z x (Ia - Ib)), so that if one primary phase has low voltage it will still cause an imbalance on the motor. The breaker and motor protection will protect them and us either way.
Am I thinking correctly? Suggestions? Thank you much.