connections for AC Hi pot test

Status
Not open for further replies.

zaza123

Electrical
Dec 3, 2008
103
I am doing AC Hi pot test , the euipment i am using is Baur.for the AC Hi pot test of three cables (Motor cables) should i connect all the cables together and apply hi voltage or should i connect one cable for highvoltage & the remaining cables to ground. i dont have standards with me but the test we are doing is as per standard cenelec HD 620,621 , VDE DIN 0276-620, 621.
But whatever may be the standard the connections procedure will be same.
Waiting for all the replies
thanks & regards
 
Replies continue below

Recommended for you

If you want to test the integrity of the cables(conductors) to ground only, you may connect the three cables(conductors) together. If you wish to check the insulation of the cables(conductors) to ground AND to each other, test one cable(conductors) at a time with the other cables(conductors) grounded.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 