tulum
Industrial
- Jan 13, 2004
- 335
We have a 25kva transformer that is being switched by a contactor on the primary with a magnet as a load (long story).
It has been in use for 5 years, however to now get it engineered approved we need to upsize the contactor.
What is the reason for this? The contactor was rated according to motor loads rather than a xfrm load. My first thought was that a motor load has approximately 6-8xFLC inrush, where as a xfmr has 12-25xFLC. However, when you do the math the contactor should still hold. Then I thought maybe it is because a xfmr is more inductive than a motor, and would inturn produce more stress on the contacts during parting, and hence limit the life of the contactor?
Any ideas??
It has been in use for 5 years, however to now get it engineered approved we need to upsize the contactor.
What is the reason for this? The contactor was rated according to motor loads rather than a xfrm load. My first thought was that a motor load has approximately 6-8xFLC inrush, where as a xfmr has 12-25xFLC. However, when you do the math the contactor should still hold. Then I thought maybe it is because a xfmr is more inductive than a motor, and would inturn produce more stress on the contacts during parting, and hence limit the life of the contactor?
Any ideas??