Chemical
Nov 17, 2002
1
Folks,

I am using a 40A motor contactor to energize a circuit with the following components:

4 motors each rated for 208V, ¾ HP, 5.2 FLA (manufacturer’s info)
1 motor rated for 208 V, 1/3 HP, 2.3 FLA (manufacturer’s info)
and a total of 14 A non-motor load (mini-fan, ballast, horn, indicating lights, ...)

Isn’t it a misapplication to use a motor contactor to energize non-motor loads? I am using a Square D contactor SC02 type. Many thanks for your comments, -Mort
 
Replies continue below

Recommended for you

A quick look at the data sheet ( indicates that your contactor is only rated for either 27 or 36 amps, not the 40 amps that you state. Those lower ratings could be a problem.

Otherwise, it's OK to use a motor contactor for the loads you indicate. Motors are, generally speaking, a "difficult" load to start due to their inductive nature, compared to other resistive loads such as lights, heaters, etc. You can use a motor contactor to control resistive loads, but you cannot use a general purpose contactor to start a motor, at least not without proper derating.

Make sure you have provided overload and short circuit protection for all loads per code requirements. And double check the rating of your contactor as I mentioned above.
 
To my way of thinking I would have individual motor starters for each motor or at least a single properly rated contactor with individual overload relays for each motor and a seperate contactor for the non motor load. That would provide the proper overload protection for the motors.
 
P.S. The above installation would also easily facilitate troubleshooting of an overload trip condition. The tripped motor(s) would be obvious.
 