umrce
Structural
- Jun 14, 2011
- 47
This is an incredibly tedious question so bear with me.
I'm trying to terminate some negative moment reinforcement and AASHTO Section 5.10.8.1.2c states that At least one third of the total tension reinforcement provided for negative moment at a support shall have an embedment length beyond the point of inflection not less than the greast of the following....
The bars I'm terminating are #5's @ 6" but instead of taking them out to the inflection point, I was going to terminate them early (per the general requirements of 5.10.5.1.2a) and use the continuous temperature and shrinkage reinforcement (#4's @ 12") to meet the 1/3 requirement.
Unfortunately 1/3 of 0.62 in^2 is 0.207 in^2/ft so a #4 @ 12" violates this ever so slightly. Would any of you be OK with this? I don't feel I can justify basing it on the required steel because the code clearly states that the 1/3 is based on the total steel provided, not required.
I'm trying to terminate some negative moment reinforcement and AASHTO Section 5.10.8.1.2c states that At least one third of the total tension reinforcement provided for negative moment at a support shall have an embedment length beyond the point of inflection not less than the greast of the following....
The bars I'm terminating are #5's @ 6" but instead of taking them out to the inflection point, I was going to terminate them early (per the general requirements of 5.10.5.1.2a) and use the continuous temperature and shrinkage reinforcement (#4's @ 12") to meet the 1/3 requirement.
Unfortunately 1/3 of 0.62 in^2 is 0.207 in^2/ft so a #4 @ 12" violates this ever so slightly. Would any of you be OK with this? I don't feel I can justify basing it on the required steel because the code clearly states that the 1/3 is based on the total steel provided, not required.