katwalatapan
Electrical
- Aug 9, 2011
- 153
Hello,
I'm working through a scenario where we have one (1), motor control panel controlling three (3), effluent pumps, in a lead-lag operation. Each effluent pump is 1/2 HP, 240V, 1-phase, 7 Amp. FLA. The motor control panel is rated to control the applicable three (3), effluent pumps.
I wanted to inquire if the electrical code may allow using one (1), 40A, 1-phase, 2-Pole branch circuit and over-current protection to feed all the three (3), effluent pumps via splicing/tapping. Also, the main feeder would be rated at 40A, however the tapped conducters to feed each pump would be rated at 20A because the pump FLA is 7 Amps. Is this acceptable or do the tapped conductors to feed each pump is also required to be rated for 40A?
Thank you.
I'm working through a scenario where we have one (1), motor control panel controlling three (3), effluent pumps, in a lead-lag operation. Each effluent pump is 1/2 HP, 240V, 1-phase, 7 Amp. FLA. The motor control panel is rated to control the applicable three (3), effluent pumps.
I wanted to inquire if the electrical code may allow using one (1), 40A, 1-phase, 2-Pole branch circuit and over-current protection to feed all the three (3), effluent pumps via splicing/tapping. Also, the main feeder would be rated at 40A, however the tapped conducters to feed each pump would be rated at 20A because the pump FLA is 7 Amps. Is this acceptable or do the tapped conductors to feed each pump is also required to be rated for 40A?
Thank you.