esanders
Mechanical
- Mar 1, 2007
- 1
I'm working on evaluating existing pressurization systems for several control rooms and petrochemical labs. Due to the classification the inside pressure must be maintained at 0.1 in wc, also with all doors open the face velocity across the openings must be at 60 fpm. During meeting the 60 fpm requirement the pressure inside the space is allowed to fall below the 0.1 in w.c.
I calculated the cfm needed to meet the 60 fpm across all door openings but I'm not sure how to go about calculating the cfm required to maintain 0.1 in w.c.
Is meeting the 60fpm airflow adequate?
How do I calculate the amount of air needed to maintain 0.1 in w.c. while the doors are closed?
I calculated the cfm needed to meet the 60 fpm across all door openings but I'm not sure how to go about calculating the cfm required to maintain 0.1 in w.c.
Is meeting the 60fpm airflow adequate?
How do I calculate the amount of air needed to maintain 0.1 in w.c. while the doors are closed?