Hi. I'm new here, so my first question concerns a problem we've had with a control valve. First, a few details:
Valve is used in a spillback system on a Refinery Crude Unit. The valve is on a line from the discharge vessel (we'll call it vessel 3, operating pressure 6-7kg/cm) of a compressor back to the suction vessel (Vessel 2, operating pressure approx 1kg/cm). The valve is controlled from a pressure transmitter (via Honeywell TDC & 4-20mA o/p, then i/p) on another vessel ('vessel 1') which is linked to vessel 2 with a common line.
When the pressure drops too low on vessel 1 (and equally low on the vessel 2) the valve should open to recirculate the gas and thus increase the pressure in vessels 1&2.
The product is C3/C4s. Uncertain of the temperature its at, but it makes the pipework warm to touch, so obviously fairly hot (will post temp when I've checked).
The valve is a 3" Blakeborough BV(500 or 900) globe valve, =% plug, air fail closed, air on top of actuator to open (spring forces valve up to close).
The issue with the valve is that operations have been claiming that the valve will not control and believe there is no flow through the line. The valve is awkward to check as it is in split-range control with a second valve which opens to flare if vessel 1 pressure rises too high, so operations are uncomfortable to allow tests without full written procedures etc. However I am certain that the valve stem is moving, so I thought it was possible the stem was snapped inside or valve plug jammed.
Thermography was carried out on the valve and put the temperature of the body upstream at 27 deg C and downstream at 11 deg C, although I suspect the upstream body temp is higher than that.
Process engineers then had both gate block valves and the control valve body x-rayed. This shows that the block valves are both clear. It also more importantly shows that the valve plug is not seated in the valve, so I believe that it is physically open.
When the bypass valve was opened I have been told (although as I did not witness this I do not know how far open the valve was) the downstream temperature increase.
Has anyone got any suggestions as to what could be the issue? I suspect that the difference in temperature is due to the Joule-Thomson effect, and that opening the bypass valve (which I believe is a gate valve?) the D.P. was reduced so the temperature changed stopped.
However I cannot figure out why the valve is not having any control. Is it possible the gas is cooling to the point of icing up around the plug, reducing flow?!? Or could the wrong plug type be causing this? Any suggestions?
Removing the valve for inspection sounds obvious, but it is positioned awkwardly with little access to use a crane. I'm thinking about trying to block it in and drop the bottom flange off the valve to check inside, but again this will require a mountain of paperwork to do.
Valve is used in a spillback system on a Refinery Crude Unit. The valve is on a line from the discharge vessel (we'll call it vessel 3, operating pressure 6-7kg/cm) of a compressor back to the suction vessel (Vessel 2, operating pressure approx 1kg/cm). The valve is controlled from a pressure transmitter (via Honeywell TDC & 4-20mA o/p, then i/p) on another vessel ('vessel 1') which is linked to vessel 2 with a common line.
When the pressure drops too low on vessel 1 (and equally low on the vessel 2) the valve should open to recirculate the gas and thus increase the pressure in vessels 1&2.
The product is C3/C4s. Uncertain of the temperature its at, but it makes the pipework warm to touch, so obviously fairly hot (will post temp when I've checked).
The valve is a 3" Blakeborough BV(500 or 900) globe valve, =% plug, air fail closed, air on top of actuator to open (spring forces valve up to close).
The issue with the valve is that operations have been claiming that the valve will not control and believe there is no flow through the line. The valve is awkward to check as it is in split-range control with a second valve which opens to flare if vessel 1 pressure rises too high, so operations are uncomfortable to allow tests without full written procedures etc. However I am certain that the valve stem is moving, so I thought it was possible the stem was snapped inside or valve plug jammed.
Thermography was carried out on the valve and put the temperature of the body upstream at 27 deg C and downstream at 11 deg C, although I suspect the upstream body temp is higher than that.
Process engineers then had both gate block valves and the control valve body x-rayed. This shows that the block valves are both clear. It also more importantly shows that the valve plug is not seated in the valve, so I believe that it is physically open.
When the bypass valve was opened I have been told (although as I did not witness this I do not know how far open the valve was) the downstream temperature increase.
Has anyone got any suggestions as to what could be the issue? I suspect that the difference in temperature is due to the Joule-Thomson effect, and that opening the bypass valve (which I believe is a gate valve?) the D.P. was reduced so the temperature changed stopped.
However I cannot figure out why the valve is not having any control. Is it possible the gas is cooling to the point of icing up around the plug, reducing flow?!? Or could the wrong plug type be causing this? Any suggestions?
Removing the valve for inspection sounds obvious, but it is positioned awkwardly with little access to use a crane. I'm thinking about trying to block it in and drop the bottom flange off the valve to check inside, but again this will require a mountain of paperwork to do.