Pruk
Electrical
- Oct 28, 2008
- 4
I just read an article about control valve leakage calculation details below.
Cv max = 182, Flow rate at 100% open = 50 MMScfd
The valve is ANSI class IV specification. So design leakage will be 0.01 % at 50 psi(roughly).
Leakage at 50 psi = 0.01/100 * 50 MMScfd = 0.005 MMScfd
If inlet pressure is 1800 psi.
Then, the maximum leakage at 1800 psi differential
= 0.005 * sqrt(1800/50)
= 0.03 MMScfd
I'm not sure why they have to use sqrt in the equation. If you have any ideas please share them.
Thanks
Cv max = 182, Flow rate at 100% open = 50 MMScfd
The valve is ANSI class IV specification. So design leakage will be 0.01 % at 50 psi(roughly).
Leakage at 50 psi = 0.01/100 * 50 MMScfd = 0.005 MMScfd
If inlet pressure is 1800 psi.
Then, the maximum leakage at 1800 psi differential
= 0.005 * sqrt(1800/50)
= 0.03 MMScfd
I'm not sure why they have to use sqrt in the equation. If you have any ideas please share them.
Thanks