Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Control Valve minimum body size

Status
Not open for further replies.

Instr13

Electrical
Jun 3, 2002
12
0
0
US
Hi,
In many specifications of refineries (Oil&Gas), the minimum body size of Control Valves specified as 1 in and 300# class regardless of Pipe size and specification. Could anyone give me an explanation.
I am trying to replace a 1/2" pressure regulator with a control valve therefore I am thinking of using 1/2" body control valve and 150# flange (deviating from normal practice).
Thanks.
 
Replies continue below

Recommended for you

it has to do with valve body/piping strength in an operating environment, fire protection, and a desire to minimize the stocking of fractional sizes. the flange ratings are another matter.

if you are in a process line stick with the spec.


 
Think you can live with evry one in peace by using a reduce port 1" V-ball valve or using a 1" globe valve with low Cv value. (for 1/2" control valve a butterfly is out of the question anyway).
 
Status
Not open for further replies.
Back
Top