sheiko
Chemical
- May 7, 2007
- 422
Hello,
I have heard of three alternate methods (vs the traditional one consisting of allowing 50 to 25% of the system frictional pressure drop excluding itself to the control valve) to determine the allowable pressure drop across a control valve during the design stage:
1/ Connell's one using a formula that everyone knows
2/ A method consisting of assigning a minimum pressure drop (10 or 15 psi) at its maximum expected design flowrate and at a upper opening limit 80%. This method has been presented by Frank Yu in "Easy way to estimate realistic control valve pressure drops" issued August 2000 in HP.
3/ Also, in section 3.7 - chapter 3 of the very good free ebook available at It is recommended to assume a pressure head drop across the valve of 10 ft of fluid at its maximum expected design flowrate and at a upper opening limit 90%.
My feeling is that the Connell's one is more rigorous as the notion of controllability is incorporated in the equation, but in the article corresponding to the second method, Mr YU concludes that his method is better than the Connell's one (from an economical point of view namely)...
A/ Then i would like to know if some experienced engineers could tell me which one they would recommend and why?
AND their feeling on the third method?
B/ Also, I would like to know the origin of the methods 2/ and 3/, i.e. why 10-15 psi or 10 ft of fluid? why these values?
"We don't believe things because they are true, things are true because we believe them."
"Small people talk about others, average people talk about things, smart people talk about ideas and legends never talk."
I have heard of three alternate methods (vs the traditional one consisting of allowing 50 to 25% of the system frictional pressure drop excluding itself to the control valve) to determine the allowable pressure drop across a control valve during the design stage:
1/ Connell's one using a formula that everyone knows
2/ A method consisting of assigning a minimum pressure drop (10 or 15 psi) at its maximum expected design flowrate and at a upper opening limit 80%. This method has been presented by Frank Yu in "Easy way to estimate realistic control valve pressure drops" issued August 2000 in HP.
3/ Also, in section 3.7 - chapter 3 of the very good free ebook available at It is recommended to assume a pressure head drop across the valve of 10 ft of fluid at its maximum expected design flowrate and at a upper opening limit 90%.
My feeling is that the Connell's one is more rigorous as the notion of controllability is incorporated in the equation, but in the article corresponding to the second method, Mr YU concludes that his method is better than the Connell's one (from an economical point of view namely)...
A/ Then i would like to know if some experienced engineers could tell me which one they would recommend and why?
AND their feeling on the third method?
B/ Also, I would like to know the origin of the methods 2/ and 3/, i.e. why 10-15 psi or 10 ft of fluid? why these values?
"We don't believe things because they are true, things are true because we believe them."
"Small people talk about others, average people talk about things, smart people talk about ideas and legends never talk."