I may be talking out of turn here, but don't you need to establish the speed of operation for the valve service and then taylor the actuator to achieve the duty?
If however you have the control arrangement you mention already in service then the best way to check the speeds of operation is to physically open and close the valve.
1. Formula to try is as follows;
V = Displacement of actuator (in³)
C = Constant factor (80psig = 0.480)
t = Required stroking time (seconds)
Cv = Flow coefficient
t = V x C / Cv x 29
OR
V = t x Cv x 29 / C
2. You don't need to consider the spring as one the pressure is below 80 psig the spring is assisting closure. Equally you should note that any excess pressure above 80psig is detrimental to your speed of closure, i.e., until the pressure is down around the 70psig mark, the actuator will remain open so although you have initiated closure the valve has not necessarily moved for several seconds. As I said in my earlier thread this can be overcome by fitting Quick Exhaust Valves at the actuator inlet ports to get the air out quickly in order to speed up the closure.