powerhigh
Industrial
- Jul 14, 2003
- 5
I am working out a control solution for a load switching application, and I'm much more qualified as a 20 yrs+ controls eng'r than power, where I have minimal experience - hence, I need some assistance, please.
I'm working with a heating system with 3 pairs of independantly controlled resistive loads. These are on the secondary of a D-Y that is 480/80. There is a need to selectively current limit the primary to either 60 or 100A.
The six loads, two on each point of the wye, are controlled by a six zone on/off temperature/process controller.
I have used three single-phase phase angle controllers on the primary - using only the current limit function. These have fixed compensation for phase shift included. Two problems surfaced: first, with different combinations of the 6 loads turned on/off there were secondary V variations, both high & low. These on their own are acceptable to the process, albeit undesirable.
Second, and more significantly (I think) is what happens as the loads are nearly all, or all switched off. Then the load resistance change makes for a change in the primary load inductance and my SCR controller's phase shift compensation is off. This leaves a nice measurable amount of reactive power in the primary. Also, switching loads on and off when there are only one or two in use has blown 200A slo-blo supply fuses, although none of the controllers or SCR's have been damaged.
Perhaps I am going about this the wrong way.
Is there an accepted method to limit current with this D-Y, six load configuration?
I am considering controlling the 6 loads with contactors and SCR's for soft starts and stops while measuring the current in series w/ the primary lines. With some logic, I intend to prioritize the loads so as to control max current. Even if this works, how can I calculate the primary currents to expect for all 36 (6 x 6) load on/off combinations?
Thanks in advance.
Chris
I'm working with a heating system with 3 pairs of independantly controlled resistive loads. These are on the secondary of a D-Y that is 480/80. There is a need to selectively current limit the primary to either 60 or 100A.
The six loads, two on each point of the wye, are controlled by a six zone on/off temperature/process controller.
I have used three single-phase phase angle controllers on the primary - using only the current limit function. These have fixed compensation for phase shift included. Two problems surfaced: first, with different combinations of the 6 loads turned on/off there were secondary V variations, both high & low. These on their own are acceptable to the process, albeit undesirable.
Second, and more significantly (I think) is what happens as the loads are nearly all, or all switched off. Then the load resistance change makes for a change in the primary load inductance and my SCR controller's phase shift compensation is off. This leaves a nice measurable amount of reactive power in the primary. Also, switching loads on and off when there are only one or two in use has blown 200A slo-blo supply fuses, although none of the controllers or SCR's have been damaged.
Perhaps I am going about this the wrong way.
Is there an accepted method to limit current with this D-Y, six load configuration?
I am considering controlling the 6 loads with contactors and SCR's for soft starts and stops while measuring the current in series w/ the primary lines. With some logic, I intend to prioritize the loads so as to control max current. Even if this works, how can I calculate the primary currents to expect for all 36 (6 x 6) load on/off combinations?
Thanks in advance.
Chris