rockman7892
Electrical
- Apr 7, 2008
- 1,161
A wastewater plant that I am currently involved with operates their 4.16kV system solidly grounded. Two of their other plants are impedance grounded however for whatever reason this particular one is solidly grounded. (70's vintage plant)
I have approached the customer recently with discussions regarding converting the solidly grounded system to a LRG system and explained the benefits of doing so (reduced equipment damage, personnel safety, etc....)
The service entrance transformers to the plant are utility owned and are 13.2kV - 4.16kV Y-Gnd/Y-Gnd transformers. They are actually four 2500kVA transformers in parallel which make up a 10MVA service (There are two identical service entrances into M-T-M Switchgear).
Before I pursue this any further I have a few concerns that I was hoping others may have experience with.
1) Are you able to impedance ground the secondary of a Y-Gnd / Y-Gnd transformer ore are the implications that prevent you from doing so? All the LRG/HRG systems I have ever seen have been from a Delta/Wye transformer.
2) Can an LRG be implemented with a case like this where there is not a single transformer but rather 4 transformers each most likely having a neutral? Is it possible to bring all of the neural points to a common point before inserting a LRG? (I'm not that familiar with paralleled transformer configurations for utility services)
3) Seeing that these are utility owned transformers do utilities typically allow impedance grounding of the secondary if it is possible with the Y/Y configuration?
Thanks
I have approached the customer recently with discussions regarding converting the solidly grounded system to a LRG system and explained the benefits of doing so (reduced equipment damage, personnel safety, etc....)
The service entrance transformers to the plant are utility owned and are 13.2kV - 4.16kV Y-Gnd/Y-Gnd transformers. They are actually four 2500kVA transformers in parallel which make up a 10MVA service (There are two identical service entrances into M-T-M Switchgear).
Before I pursue this any further I have a few concerns that I was hoping others may have experience with.
1) Are you able to impedance ground the secondary of a Y-Gnd / Y-Gnd transformer ore are the implications that prevent you from doing so? All the LRG/HRG systems I have ever seen have been from a Delta/Wye transformer.
2) Can an LRG be implemented with a case like this where there is not a single transformer but rather 4 transformers each most likely having a neutral? Is it possible to bring all of the neural points to a common point before inserting a LRG? (I'm not that familiar with paralleled transformer configurations for utility services)
3) Seeing that these are utility owned transformers do utilities typically allow impedance grounding of the secondary if it is possible with the Y/Y configuration?
Thanks