I got a 500KVA, Delta/Star transformer supplying a 3 phase 3 wire heater load in our chemical process plant which suffered recurring failures. Per observations of failure mode - it seemed to be a result of transient high voltage typical of ungrounded system.
With measured system charging current to only 0.37Amp, required neutral resistance is calculated to 561.75Ohm (=360/SQRT(3)/0.37A). To me, 600Ohm, 150Watt resistance should serve the purpose, at least theoretically ?! Or is this a too small a system to go HRG way.
I have no previous experience of such conversion and seeking second opinion.