Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

cooling coil

Status
Not open for further replies.

AO1958

Industrial
Mar 13, 2009
73
Hello there

I am facing to following topic.
Very specific, and old post can't help me, unfortunately.

I am dealing with a cooling coil, and volumetric air flow at OUTLET is given to me.

Known data are:
- air inlet temperature
- air inlet relative humidity
- coil capacity

It is a strange problem:
- since air I estimate there will be dehumidification I assume mass flow won't conserve.
Therefore I can't calculate air outlet mass flow and consider it constant.

Any suggestion of how determining inlet volumetric air flow ?

Many thanks !
 
Replies continue below

Recommended for you

The volumetric inlet flow = volumetric outflow.

From conservation of mass, inlet lb/hr = outlet lbs/hr-condensate removed.

If outlet air wet bulb is known, the latent heat removal can be calculated and thus lb/hr of condensate removed.
Otherwise, no unique solution, since outlet wet bulb depends on latent capacity of the cooling coil.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor