I currently have process water @ 500gpm that is cooled via a cooling tower from about 110 down to 90 F. Our process requirements have changed, and we now need the process water to be at a lower temperature, approx. cooled from 100 down to 75-80 F.
My concern is whether a cooling tower is capable of reaching the 75-80 degree temperature year round. The plant is located in Toronto, Ontario, Canada, so the wetbulb temperature can climb into the 60's for 2-3 months of the year. Also, the wetbulb can hit into the 70's during the late afternoon hours in July-August.
My question:
Will adding additional cooling tower capacity meet my requirements, or does the cooling tower's performance severly degrade when the wetbulb temp is so close to my design cooling temp?
Maybe for this design temperature, it would be better to purchase a chiller to couple with the cooling tower?
Some general discussion on the topic would be great, I'm not looking for an easy answer.
Thanks,
Grant
I currently have process water @ 500gpm that is cooled via a cooling tower from about 110 down to 90 F. Our process requirements have changed, and we now need the process water to be at a lower temperature, approx. cooled from 100 down to 75-80 F.
My concern is whether a cooling tower is capable of reaching the 75-80 degree temperature year round. The plant is located in Toronto, Ontario, Canada, so the wetbulb temperature can climb into the 60's for 2-3 months of the year. Also, the wetbulb can hit into the 70's during the late afternoon hours in July-August.
My question:
Will adding additional cooling tower capacity meet my requirements, or does the cooling tower's performance severly degrade when the wetbulb temp is so close to my design cooling temp?
Maybe for this design temperature, it would be better to purchase a chiller to couple with the cooling tower?
Some general discussion on the topic would be great, I'm not looking for an easy answer.
Thanks,
Grant