Water cooled condenser ratings are usually published in tons of heat rejection at specified entering water temperature, water flow rate per ton, and condensing temperature. ARI Standard 450 specifies 85°F water entering, 95°F water leaving, and 105°F condensing temperature as the basis for ratings, but does not define a ton of heat rejection. So if we use 15,000 Btu/hr which is the commonly used ton of HR in water cooled condenser. On this basis, the standard water flow rate per ton can be calculated as follows:
CHR (Btu/hr) = gpm x 500 x °F water temperature rise, or delta “T”
For 15,000 Btu/hr CHR per ton, and 10° water temperature rise, 3 gpm per ton is the required flow rate. Example: 15000btu/hr/500x10degrees = 15,000/ 5,000 = 3gpm
Now with closed circuit coolers(evaporator) operation of the system is calculated a little different because it’s based on a heat rejection of 12,000btu/hr, so using the same formula it becomes 12,000btu/hr/500x10 degrees = 2.4gpm. The extra 3,000 btu/hr in the condenser is a gain mostly from the heat of compression of the refrigerant in the compressor. Now you may ask where does the 500 number come from ,well 500 represents the number of lbs of water circulated in 1 hour or 8.333lbs x 60 minutes = 500 lbs. Hope this is helpful