Historic building and you aim at 30% over ASHRAE with WSHP? Highly questionable, as you stand, you will have a hard time meeting ASHRAE 2007, let alone beating it by 30%.
You did not say if this was residential or commercial, and you did not mention your total load - System choice in Appendix G depends a lot on application and load limits.
I suggest the following:
1. Forget about WSHP, when it gets cold, the electric heat kicks in and takes over your WSHP. You will have a high electric consumption, gooes against LEED.
2. For such an application, I highly recommend that you go Chilled water with MODULAR chillers (there is always space for modular chillers), step down chillers by turning chillers OFF. Nothing beats OFF, you should get around 0.5 KW/ton and a lower IPLV than centrifugal chillers, VFD on CHW, CV on CW to the tower.
3. Why glycol for the tower? just heat the basin.
4. You can even get air-cooled modular chillers in place of the cooling towers, and you will do better and cheaper. The IPLV on air-cooled modular chillers is comparable to centrifugal chillers efficiency.
5, I'd use condensing boilers along for a 4-pipe system.
6. I'd use a total enthalpy wheel for all OA
7, If you can replace the windows with Low-E glass and get some kind of Lutron type dimmers on lighting (total 0.6 W/SF), daylight harvesting, occupancy sensors, DCV, etc. so much the better.
Then you may be NEAR 30% over ASHRAE 2007.