I recommend against this!!! I completely understand the thinking and have installed systems that way. However, I have learned the hard way that this can lead to problems. I had a system of 4 towers in parallel with only isolation valves on the inlet lines. When the tower closest to the pumps was isolated,the basin would get sucked dry faster than the equalizer line could keep up. Low water sensors in that tower would then open the makeup valve. For reasons of customer preference, the makeup water did not go directly to each tower but instead was injected into the main. This caused the active towers to overflow. So perhaps a larger equalizer would have prevented this, but we instead went back and installed actuators on the tower discharge valves.