StoneCold
Chemical
- Mar 11, 2003
- 992
I have a cooling water blowdown question. Does anyone have a rule of thumb about the amount of blowdown water from a cooling tower? I know that usually conductivity is the controlling factor but I would like to know if there is any design rule out there that relates the amount of makeup water to the amount of blowdown. I know that the conductivity of the makeup water is about 60 mho's and we are trying to keep our cooling water conductivity below 1500 mhos. So at minimum I need to blow down 1500/60=1/25 . One gallon of blowdown water for every 25 gallons of makeup water. But in reality lots of stuff gets sucked into the tower, etc and the ratio must be lower like one gallon of blowdown for every 10 gallons of makeup water.
In the end I am only looking for a rough number to tell my boss that we made up xxx gallons this week and we need to blow down xxx gallons.
The quantity is an issue because we are having to truck the blowdown water off right now instead of being able to dump it to city sewer.
Thanks
StoneCold
In the end I am only looking for a rough number to tell my boss that we made up xxx gallons this week and we need to blow down xxx gallons.
The quantity is an issue because we are having to truck the blowdown water off right now instead of being able to dump it to city sewer.
Thanks
StoneCold