Cooling water temperature rise

Status
Not open for further replies.

edison123

Electrical
Oct 23, 2002
4,467

What is the normal temperature rise (Outlet water temp - inlet water temp)in air-to-water cooled machines ? I had always assumed it to be 2-3 deg C. But in one generator, it is around 6 deg C. Flow rate & pressure are normal as per name plate. Does this mean the coolers have insufficient capacity ?


* Basically, I would like a full-time job on part-time basis *
 
Replies continue below

Recommended for you

If you have a higher rise across the generator then it has nothing to do with the chiller. It means the generator is wasting more heat for some reason.

Keith Cress
Flamin Systems, Inc.-
 
Thx itsmoked. But it is a OEM designed cooler. So, they should know their generator losses and should design their coolers accordingly.

I am still keen to know what is the normal temp difference between outlet & inlet water. Any field experience or standards would help.


* Basically, I would like a full-time job on part-time basis *
 
Hi Edison123.

The temperature rise will depend on the amount of heat losses and the water flow. For water,
1cal/1gr = 1°C rise
The guideline figures I have are:
AT 80 F incoming cooling water provide 0.85 GPM per each 1 kW loss for around 4.5° C water temperature rise.
The recommended water flow ratio increases or reduces with water temperature, 0.68 GPM for 70F; 1.15 GPM for 95F. However the water temperature rise is not constant if those ratios are followed.
 
Generally, heat transfer devices are designed for a dT of 50C for optimizatin of the HX size. Though, the rule varies from case to case, it is a good approximation.

 
for some reason all the coolers I have been involved wioth were designed for 6C, so seems ok.
flow (l/s)= 0.24 x losses (kW)/water rise

 
Thank you all for the posts. I take it that 6 deg C rise is normal.


* Basically, I would like a full-time job on part-time basis *
 
Our design winds up at about 6º to 10º rise. There is some trade-offs between the lowering the operational temperature of unit versus the outlet temperature and amount of water/pumping infrastructure to maintain a substantially lower outlet temperature.

In your example, the difference between designing for a 3º versus a 6º delta is essentially doubling the coolant flow. Therefore, while the unit might operate at a lower temperature, the pumping system is working twice as hard.

Different designers might well pick different design points, based on their unit's capabilities and liabilities.

TTFN



 
Hi edison123
If the temperature rise is higher than similar transformers in your plant you may have more losses or a flow restriction.
This may also be an indication of circulating currents, harmonics, or a flux problem (possibly caused by harmonics).
If you circulation is temperature controlled you may have a bad sensor. You may also have thermometer errors.
Or, everything may be normal.