bdn2004
Electrical
- Jan 27, 2007
- 794
Attached is out of the 1986 Buff Book in the Coordination Section example. It's a Main (green) and a Feeder Breaker (yellow)on a 480V switchgear and the 100A molded case circuit breaker on the very bottom (white).
I notice that the Feeder Breaker starts to trip at 0.1 seconds delay. In other words it's out of the instantaneous range. To me this makes sense, as the small MCCB out on the floor will have a chance to act. Is this still logical in 2020 ? Or has arc-flash made this method obsolete?
I'm looking at an existing study and all of the feeder breakers have instantaneous settings that will all conflict with all downstream devices - and the whole circuit will be shut down as a result of a short circuit.
I notice that the Feeder Breaker starts to trip at 0.1 seconds delay. In other words it's out of the instantaneous range. To me this makes sense, as the small MCCB out on the floor will have a chance to act. Is this still logical in 2020 ? Or has arc-flash made this method obsolete?
I'm looking at an existing study and all of the feeder breakers have instantaneous settings that will all conflict with all downstream devices - and the whole circuit will be shut down as a result of a short circuit.