VYCanisMajoris

Mechanical
Nov 12, 2024
1
Hi Everyone. i am doing a solidworks flow for a cold plate. SImiliar to the one in the picture. Aluminium base plate and copper tube with 50/50 glycol water mix. I need to determine the COP of the plate for different flowrates. According to my understanding COP= Qout/Win and Win can be calculated as Pressure Drop x Flowrate. Both my flowrate and pressure drop is very low, 0.125 L/min (massflow=0.00225 kg/s, Re=133) and around 300 Pa and with a Qout of around 100 W this results in very High COP which doesn't make sense when compared to other systems. Am I understanding something wrong or is it just because of the low flow rate and pressure drop? WHat is a better way to determine COP for a plate like this.1731424534123.png
 
Replies continue below

Recommended for you

You have to consider the entire work required to produce the refrigeration effect. Most of the work is typically the work of the compressor in a cooling system but includes all energy input such as evaporator fans, etc.
 