gonefishn
Mining
- Apr 14, 2009
- 5
We have a large capacity closed hydronic heating system charged with 50/50 blend of propylene glycol and demin water. The glycol/water is about 10 years old and was never properly inhibited until about 7 months ago. Prior to inhibiting, the glycol/water was tested and found to have a pH of about 6.0 and a reserve alkalinity of 0. In the lab it was determined that the dissolved iron could be dropped out and the pH readily raised with an inhibitor (molybddate/triazole/phosphate type). We drained the system, inhibited the glycol/water, and returned it to the system (less the sludge that settled out). Afterwards the pH in the system was 8.8 and the reserve alkalinity 6.8. Recently, we removed a pump for maintenance, and in adddition to the internal parts showing significant corrosion (thick black coating presumeably oxidized CS) there was a thin plating of copper covering this black coating (see picture). We believe the corrosion was long term previous damage. The question is what does the copper plating indicate. Is it the dissolved copper that was in the uninhibited glycol/water, dropped out by the inhibitor? Or could it be some sort of new galvanic corrosion that is a result of the inhibitor? I believe the pump is a long ways from any copper in the system, i.e. many feet. Any help appreciated.