The line-to-Earth [earthing] fault calculation it is destined to check the withstand short-circuit current through main conductor and screen [sheath, armor, conduit or else]
The main conductor short-circuit current depends on screen[shield, sheath] impedance and the mutual impedance between main conductor and screen and the Earth. But even if the short-circuit it is not a ground fault the screen will get a short-circuit current by induction from the main current. This happened like in the case of continuous load current and is calculated using formula from IEC 60287-1-1 2.3.1 Two single-core cables, and three single-core cables (in trefoil formation), sheaths bonded at both ends of an electrical section. If the main losses pmain=Imain.sh.circ^2xRcond the total losses will be pmain x(1+ λ1) and screen losses only pmain x λ1.
Rs resistance depends on screen material as tapes [with overlap or gap],wire, braid, tube and other form and different metals as copper, aluminum, steel, lead and other.
For tapes with overlap [new tapes and good contact] it may be consider as tube then[ as per French Standard HN-33-S-52-for instance]:
Rs=[R1]=2.ρ1.L/(π.(d-T1).T1)
ρ1=resistivity of tape material [copper =1/58 ohm.mm^2/m at 20oC]
The maximum temperature for copper tape it could be 250 oC [for less than 5 sec]
L=cable length[m]
d=insulated core diameter [mm]
T1=tape thickness[mm]
The overlapping [%] it has a very small influence and it could be neglected.