Copper Temp

Status
Not open for further replies.

tulum

Industrial
Jan 13, 2004
335
Does anyone know what the maximum temperature is for copper bus??

We have some bus here that looks like it could achieve 200 degC during a short circuit. I am pretty sure the devices hanging off the bus are not good for more than 100 degc.

However, a co-worker said he remembers some bus off a transformer running at 300 degc? This seems extreme... ya think?

 
Replies continue below

Recommended for you

An oft-quoted ‘emergency’ temperature limit for insulated copper cables is 250°C in short-circuit calculations. I don’t know the origin of that figure—perhaps it is a judgment call where occasional excursion will not produce significant physical or electrical degradation.
 
Suggestion: It depends on a bus application. Reference: IEEE Std 141-1993 Red Book Chapter 13 Busways
 