Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Copper vs. aluminum buss duct

Status
Not open for further replies.

stevwri

Electrical
Sep 6, 2001
3
We are adding onto our manufacturing facility. One electrical design uses aluminum buss duct for 480V distribution. Another uses copper buss duct. Aside from price, what are they advantages and disadvantges of each?
 
Replies continue below

Recommended for you

Torqued aluminum connections can relax due to creep. That causes me concern. Even periodic retorquing may not be a good solution since it just accelerates the distortion of the components. I have seen some pretty distorted bus connection areas at our aluminum isophase bus connections where the washer causes an indentation into the adjacent bus section. I've never seen a failure yet but I don't like it.
 
The copper bus ducts are characterised by low resistivity and high weight, while the aluminum bus ducts are characterised by a bit higher resistivity and LOWER weight, considering the same cross section.

Usually the aluminum bus ducts are chosen when the mechanical load (weight) is a problem.
 
Suggestions:
1. It is convenient to have all copper or all aluminum buses since the transitions from copper to aluminum and vice-versa may pose some challenges. Also, connections to transformers and switchgear could pose some challenges if of dissimilar metal.
2. For the same load, the aluminum buses will be more voluminous.
3. Since the bus amp ratings are not posted, the availability of copper and aluminum buses of your required ratings should be checked.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor