unclebob
Electrical
- Sep 16, 2004
- 353
Hi! One of our customers have an oil transformer and we do a dissolve gaz analysis annually. We found that the transformer have a corona (partial discharge) problem. The key gases are hydrogen (1150 ppm)and methane (110 ppm). The level of the other gases is insignificant. The progression
of H2 is about 200 ppm/year.
Now that we know this, is there a way to find where corona is occuring? We have made a visual inspection, from the main hole and found no grey-to-black powdery traces.
The transformer is:
Northern Transformers
1 500 kVA
25 000 - 600/347 V
sealed type
1984
ONAN
Any comments?
of H2 is about 200 ppm/year.
Now that we know this, is there a way to find where corona is occuring? We have made a visual inspection, from the main hole and found no grey-to-black powdery traces.
The transformer is:
Northern Transformers
1 500 kVA
25 000 - 600/347 V
sealed type
1984
ONAN
Any comments?