Corona in oil transformer

Status
Not open for further replies.

unclebob

Electrical
Joined
Sep 16, 2004
Messages
353
Location
CA
Hi! One of our customers have an oil transformer and we do a dissolve gaz analysis annually. We found that the transformer have a corona (partial discharge) problem. The key gases are hydrogen (1150 ppm)and methane (110 ppm). The level of the other gases is insignificant. The progression
of H2 is about 200 ppm/year.

Now that we know this, is there a way to find where corona is occuring? We have made a visual inspection, from the main hole and found no grey-to-black powdery traces.

The transformer is:

Northern Transformers
1 500 kVA
25 000 - 600/347 V
sealed type
1984
ONAN

Any comments?
 
You can do a sonic scan, usually you would use an ultra-frequency sensor and trace the magnitudes around the transformer. The partial discharges will make the readings go high in the area where they are ocurring. I have used this method to successfully pinpoint where the partial discharges are coming from.
 
I assume you already checked for oil moisture content but if not that should be checked.

I agree with your diagnosis of corona but is it remotely possilbe this represents overheating. We had a transformer allowed to operate around 120-140C oil temp for several days and if memory serves me right the results were H2 and CH4 and CO and CO2.

=====================================