techmaximus
Civil/Environmental
- Jan 22, 2005
- 85
I have been inspecting rebar and PT installations for over a decade and I have the ICC Reinforced Concrete Special Inspector certificate. I have previously worked for a premier structural engineer in the SE as shop drawing review and field inspection. Now I work for a testing lab doing primarily field inspection work. Even with all of my experience there are a number of things about rebar installation and drawings that bug me and I want to ask you structural guys and gals about them. For instance…..
Column Tie Spacing for multi Story Building (read from bottom up)
2 ties Equally Spaced in Beam
Bottom of Beam
1 tie at 4”
3 spaces at 8”
Remained at 16”
3 spaces at 8”
1 tie at 4”
Top of Slab-on-Grade
Columns are “pre-tied” horizontally on a rack on the ground. The rodbuster starts the spacing at the bottom of the column and works his way to the top. The columns are later set with the crane.
Here is my problem: once concrete is placed in the form and the form is subsequently removed I should only be able to observe TWO ties. The only TWO ties that I should be able to observe are the two ties that the rodbuster has tied on the dowels (for convenience) that are later to be equally spaced in the depth of the beam.
It is my contention that if I observe more than two ties that the required tie spacing is incorrect and steps must be taken to correct the discrepancy. The contractor has poured a number of ground level columns and I can observe THREE ties on a number of them. To me this means that the one tie required at 4” below the bottom of the beam is missing and that the next tie down could be as much as 8” below the bottom of the beam. Any columns on which I can observe 3 ties have two spaces at 8”, are missing the 1 at 4” and will have 3 in the beam.
The contractor claims (wrong headedly) that the spacing is determined by starting at the bottom of the column and working up and that a tie at 4” below the bottom of the beam may or may not occur as the beam depths vary. What!? I understand that the beam depth will affect the TOTAL number of ties on a column but the spacing should not be affected unless a beam depth not divisible by 4” was introduced.
It is my opinion that upon standing the column rebar that the layout engineer should shoot the bottom of beam elevation and determine if that one tie is going to be at 4” below bottom of beam or not and if not that the ties be adjusted until the spacing is correct.
Am I nit picking this guy as he vociferously claims or should I bring this to the attention of the engineer of record?
SCET - Techmaximus
Column Tie Spacing for multi Story Building (read from bottom up)
2 ties Equally Spaced in Beam
Bottom of Beam
1 tie at 4”
3 spaces at 8”
Remained at 16”
3 spaces at 8”
1 tie at 4”
Top of Slab-on-Grade
Columns are “pre-tied” horizontally on a rack on the ground. The rodbuster starts the spacing at the bottom of the column and works his way to the top. The columns are later set with the crane.
Here is my problem: once concrete is placed in the form and the form is subsequently removed I should only be able to observe TWO ties. The only TWO ties that I should be able to observe are the two ties that the rodbuster has tied on the dowels (for convenience) that are later to be equally spaced in the depth of the beam.
It is my contention that if I observe more than two ties that the required tie spacing is incorrect and steps must be taken to correct the discrepancy. The contractor has poured a number of ground level columns and I can observe THREE ties on a number of them. To me this means that the one tie required at 4” below the bottom of the beam is missing and that the next tie down could be as much as 8” below the bottom of the beam. Any columns on which I can observe 3 ties have two spaces at 8”, are missing the 1 at 4” and will have 3 in the beam.
The contractor claims (wrong headedly) that the spacing is determined by starting at the bottom of the column and working up and that a tie at 4” below the bottom of the beam may or may not occur as the beam depths vary. What!? I understand that the beam depth will affect the TOTAL number of ties on a column but the spacing should not be affected unless a beam depth not divisible by 4” was introduced.
It is my opinion that upon standing the column rebar that the layout engineer should shoot the bottom of beam elevation and determine if that one tie is going to be at 4” below bottom of beam or not and if not that the ties be adjusted until the spacing is correct.
Am I nit picking this guy as he vociferously claims or should I bring this to the attention of the engineer of record?
SCET - Techmaximus