Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Corroded Anchor Bolt

Status
Not open for further replies.

SKJ25POL

Structural
Mar 4, 2011
358
I have a case that the exposed portion of anchor bolt is corroded. Please attachment.
We are unsure that what's the embedded portion condition. Is it reasonable to say the embedded part of the anchor bolt is in concrete and away from oxygen and water so will be un-corroded?


Thank you
 
 http://files.engineering.com/getfile.aspx?folder=cabe1a14-5c90-4072-a63c-0196a766246b&file=Full_page_photo.pdf
Replies continue below

Recommended for you

I think that's it's reasonable to assume that the corrosion does not extend far into the concrete. I'd certainly want positive verification of that before I called a particular refurbishment complete however.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
Well, it's half the visible diameter on both anchor bolts - where you can see them.

Let's assume the hidden part of both bolts is not corroded away at all. How are you going to use the assumed "good" steel still in the concrete when the exposed bolt is already gone? (It has 1/4 the original metal area now.) weld up a new top half of the bolt to the rusted section?
 
I'm afraid without raising a little dust, you're not going to be sure.
I just had one like that (although it was likely only one bolt), and I just instructed the contractor to chip to sound bolt material and splice another one on the sound material. They're very likely low carbon steel, so welding shouldn't be a problem. Let the contactor guess how much he's going to have to chip out.
And if there's no end to the damage, well, you're going to negotiate a change order. The contractor deserves it.
 
Judging by the use of rivets, the anchor bolts don't likely meet today's standards. But it appears that they did well with the test of time.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor