Dear All,
We have two Regeneration Heaters at our Nitrogen Plant, one stay in operation and the other in stand-by mode.these heaters are used to heat waste Nitrogen above 200 deg.C and exhaust into the atmosphere. We opened Electrical Connection Box of the one heater(Already in stand-by mode for almost one year). I saw all the connection terminals (Nuts and Bolts were heavily corroded.
The stand-by heater remain isolated in the system that is Valve in block position. Only small quantity of waste Nitrogen, that is most of it oxygen remain inside heater column till it comes back in operation.
Please see these photos-1:
lately we put this heater in operation and stop the other heater. This heater was continuously working for one year. We fond its connection terminals slightly corroded. please see the following photos-2:
The copper bars in both cases were neat and clean. only nuts and bolts (I am not sure but may be of carbon steel) were corroded.
The ambient condition of our plant is here under.
now my question is that the internal tubes of heater in column are also corroded or seal due to aging (15-years), have have been deteriorated and waste nitrogen (mostly oxygen) is leaking into to connection box and causing oxidation. Please see this photo.
or this is anode-cathode reaction where carbon steel bolts are acting as sacrificial anode to protect the copper buses as cathode.
The connection box is Ex-Proof. I do not think that the external air or atmospheric oxygen enters into connection box.
Your expertise shall be highly appreciated to diagnose the true cause of this corrosion. Please feel free to ask any info you may require.
Best Regards
We have two Regeneration Heaters at our Nitrogen Plant, one stay in operation and the other in stand-by mode.these heaters are used to heat waste Nitrogen above 200 deg.C and exhaust into the atmosphere. We opened Electrical Connection Box of the one heater(Already in stand-by mode for almost one year). I saw all the connection terminals (Nuts and Bolts were heavily corroded.
The stand-by heater remain isolated in the system that is Valve in block position. Only small quantity of waste Nitrogen, that is most of it oxygen remain inside heater column till it comes back in operation.
Please see these photos-1:
lately we put this heater in operation and stop the other heater. This heater was continuously working for one year. We fond its connection terminals slightly corroded. please see the following photos-2:
The copper bars in both cases were neat and clean. only nuts and bolts (I am not sure but may be of carbon steel) were corroded.
The ambient condition of our plant is here under.
now my question is that the internal tubes of heater in column are also corroded or seal due to aging (15-years), have have been deteriorated and waste nitrogen (mostly oxygen) is leaking into to connection box and causing oxidation. Please see this photo.
or this is anode-cathode reaction where carbon steel bolts are acting as sacrificial anode to protect the copper buses as cathode.
The connection box is Ex-Proof. I do not think that the external air or atmospheric oxygen enters into connection box.
Your expertise shall be highly appreciated to diagnose the true cause of this corrosion. Please feel free to ask any info you may require.