tech sevices,
I am assuming you are talking about a condensate collection system as would be used in a District Heating system for a college or a hospital....
I believe TD2K may be wrong in guessing abou external corrosion...... This type of tank almost always fails via interal corrosion.....
Condensate collection tanks are the "classic" location for concentrated corrosion of a carbon steel system. As the condensate returns from the collection piping,it is typically about 160-200F and has absorbed oxygen producing "carbolic acid" (as I recall). This means we have a thin-walled carbon steel tank contacting a hot, oxygenated, weak acid. Most typically, the bottom nozzle corrodes away. Needless to say, the relacement market for these tanks is a good one.....
If you check with some of the vendors of this type of tank, you will find out that they offer premium interior coatings, heavy duty wall constuction and even an "all stainless" version of this tank.
If you are replacing a tank of this type, you may also want to inspect the impellers of the pump drawing on this tank. They also become corroded away if they are of cast iron construction and have been in service any length of time.
Some websites to consider are:
- Burnham Boiler ( they make a Deaerator/collection tank combination)
- Cleaver Brooks ( deaerators)
- Armstrong International
Please give us more details!!???...... How old is the tank ?!! are there pump problems Etc.... etc
MJC