Hi
I have a corrosion meter, a 9030 Plus corrater instrument that measures the corrosion of a copper probe in mils per year. This corrosion meter is connected to a Web Master Water Controller, that reads the 4-20mA signal.
So there are two displays, one for the corrater on the other one for the controller
On the configuration panel of the corrator, I can change the “Probe rate 4-20 LOOP F/S”. This value defines the full scale for the 4-20mA. By default is 20MPY.
If I change this value to 1 for instance, the reading in the corrater stays the same but the reading in the controller is multiplied by 20.
I guess that this is changing the scale of the 4-20 signal. My questions are:
What is this value for? I mean, how do I know which is the correct value? The corrater determines the corrosion rate measuring the current between the two electrodes. Why should that current be multiplied by a factor?
It is confusing also that when I change this value (Probe rate 4-20 LOOP F/S), the readings on the corrator stays the same and the readings on the controller change.
As far as I know, the only way I have to check that corrator is working fine is replacing the copper probes and checking that the value is going to near zero.
Any help regarding corrosion meters will be highly appreciated
Best regards
I have a corrosion meter, a 9030 Plus corrater instrument that measures the corrosion of a copper probe in mils per year. This corrosion meter is connected to a Web Master Water Controller, that reads the 4-20mA signal.
So there are two displays, one for the corrater on the other one for the controller
On the configuration panel of the corrator, I can change the “Probe rate 4-20 LOOP F/S”. This value defines the full scale for the 4-20mA. By default is 20MPY.
If I change this value to 1 for instance, the reading in the corrater stays the same but the reading in the controller is multiplied by 20.
I guess that this is changing the scale of the 4-20 signal. My questions are:
What is this value for? I mean, how do I know which is the correct value? The corrater determines the corrosion rate measuring the current between the two electrodes. Why should that current be multiplied by a factor?
It is confusing also that when I change this value (Probe rate 4-20 LOOP F/S), the readings on the corrator stays the same and the readings on the controller change.
As far as I know, the only way I have to check that corrator is working fine is replacing the copper probes and checking that the value is going to near zero.
Any help regarding corrosion meters will be highly appreciated