Corrosion Resistant, Code Compliant Steam Piping bolts

Status
Not open for further replies.

PagoMitch

Mechanical
Sep 18, 2003
66
I am the engineer at the hospital in American Samoa, located about half way between Hawaii and New Zealand. The hospital is at 17 feet above sea level, and half a mile up a narrow valley. Mild steel used indoors exhibits surface rust in about 2 weeks. We replace our galvanized steel centrifugal cooling tower fan wheels annually, as they literally disintigrate and fly apart. Materials failure is a major problem.

I am specifying a rotoclave to deal with our medical waste. I visited the factory, and we are changing a lot of the hardware to 316 SS in order to deal with the corrosion.

I am trying to find corrosion resistant steam piping flange bolts/studs. We run 60PSI steam (appx 300F). My boiler rep (in Hawaii) states that ONLY ASME B31.1 classed studs are legal. There is no governing authority on-island, though I am charged with complying with US codes and standards.

A bolt vendor whom I trust in LA has suggested studs meeting A193-B8M, which are 316ss, hi tensile. He indicated that these are suitable for use up to 800F.

Could anybody with knowledge of this situation please comment? I would have thought that code compliant, corrosion resistant steam piping flange bolts would have been a little easier to find, but it seems like I'm breaking new ground here...

Thanks
 
Replies continue below

Recommended for you

Unlike your cooling tower your steam piping should not exhibit the same corrosion problems. If you have carbon steel piping/flanges I would suggest using regular B7/2H hardware. Review/revise your plant painting spec for any special needs.
 
Are you getting steam piping corrosion?
Are the lines insulated?
Are they in service all of the time?

I would rather see you use epoxy paint to protect CS than use stainless. Chloride stress cracking is a real risk if these lines ever get damp.

= = = = = = = = = = = = = = = = = = = =
Corrosion, every where, all the time.
Manage it or it will manage you.
 
Pago...

The stainless bolting/fasteners may not be the best choice. Stainless will thermally expand more than carbon steel fasters upon heat-up of the steam system.

A premium epoxy or teflon coating for the bolting may be a better choice.

There is a good discussion here:


Gimmie a star...
 
Never use male & female threads of 316 together due to the galling problem. The galling threshold for non-lubricated self-mating (same alloy) connections may be as low as 1 ksi. 18-8, 304, 304L, 316, 316L have similar fcc microstructure and very thin oxide films which breaks under shear, allowing cold-welding of the 2 parts. Further heating would make it worse, although I suggest that 300oF isn't really hot for steel or SS.

If corrosion conditions warrant stainless, connect SS items of different microstructures. E.g., 18Cr-2Ni-12Mn or Custom 455 with 304 or 316. Carpenter Technology also sells proprietary 'Gall-Tough' (UNS S20161) and 'Gall-Tough Plus' nitrogen-strengthened austenic SS which resist galling. See Carpenter Stainless Steels. Selection. Alloy Data. Fabrication.
or
[free registration required for free downloads]

You can also use an anti-seize thread lubricant to minimize galling, silver plating, pre-oxidation in air to at 1300oF to form a thicker, non-galling dark oxide, use dry film lubricant, etc.
 