Travis,
The IBC Group H-3 classification is unique because many combustible fibers are not hazardous materials, and that is the focus of the IBC requirements for Group H occupancies. However, the Group H-3 classification was assigned by the code officials because it was given such a designation in the legacy BOCA code.
When you look at the IBC requirements for a Group H3 storing combustible fibers, the only specific requirements are:
-- Automatic sprinkler protection in accordance with NFPA 13
-- A minimum one-hour fire barrier with opening protectives with an equal rating
The problem I have with the Group H classification for combustible fibers is you can be severely penalized ("dinged") on your basic allowable area. Even though its storage and the material is not a Flammable Solid, you cannot obtain a 300% area increase resulting from the sprinkler installation because of the Group H classification. Conversely, if I build a warehouse and propose rack storage of expanded, exposed Group A polystyrene, I can classify the building as a Group S-1 and make it unlimited area because its sprinklered.
I promised you a literature review. All of the data I reviewed for cotton in the Ignition Handbook was limited to baled cotton - no testing of cotton seeds was performed. When I looked for data on other agriculture seeds, I can find data for dust deflagrations and explosions, but nothing on a fire risk. I believe you can use this information along with FFP1's statements and begin to make some conservative but reasonably accurate assumptions as to commodity classification. My only comments to FFP1 statements is this: can the cotton seeds act as a free flowing material, and this potentially obstruct transverse or longitudinal flue spaces? If so, I would believe this should be included in your justification for the commodity classification.