Could you kindly give me a solution for firedamper?

Status
Not open for further replies.

aungkyawtun

Mechanical
Aug 20, 2008
32

Now I face a problem that the peneteration from ECR Room to Main Switch Board Room (A-0 Bulkhead) is 1000x400 in size.Do I need the firedamper for this peneteration?.This is the ABS Class Lifting Boat Project

 
Replies continue below

Recommended for you

You need a fire damper, if the wall being penetrated is a rated fire seperation.

The rating of the wall is generally set by the project architect, and is code driven.
 
Thanks all,I've got it.If the opening area on the A-Class bulkhead is more than 0.075 m2 there should be a firedamper
 