Cover for a reinforced concrete pipe culvert

Status
Not open for further replies.

sengr

Structural
Jul 9, 2002
11
0
0
US
Hi all. I am specifying a 18" reinforced concrete pipe culvert under a road with HS 20 loading. The pipe is barely under the base and there is no sub-base. In other words, the pipe is right below the base, with minimum thickness above the top of pipe. Is there a requirement for a minimum "cover" or distance before we could put the base above the pipe? The thickness of wear course is 3", base is 8". Thank you in advance.
 
Replies continue below

Recommended for you

The American Concrete Pipe Association has information that will help. See "Design Data 1 - Highway Live Loads On Concrete Pipe" (free .pdf download) at this link

Also, you may want to download the "Concrete Pipe Design Manual" at this link (see Chapter 4)

Finally, if it turns out that you do need more cover, perhaps an equivalent elliptical shaped pipe can be substituted for the 18" circular RCP.

[idea]
 
All tables available, that I am aware of, assume 1-foot of cover to the sub-grade. These tables identify .01 crack for a concrete pipe vs pipe classification. The loading on the pipe can be manually computed and then the required classification can be identified. These procedures are availble in the Concrete Pipe Design Manual. Check out for information. I set up a spreadsheet to automate the procedure.

Good Luck & Have Fun!
 
Seems like a pretty small pipe. I wouldn't be as worried about the pipe as the road. As BigInch says it is probably best to lay it in concrete. I would also look at adding some subbase next to the concrete so that if you have movement it is spread further.
 
If you plan on using concrete encasement, remember that over time the subgrade next to the concrete will compress creating a little depression and mound of asphalt.
 
Also, it would be wise to specify a greater strength class of concrete pipe since the cover is so shallow. Class III pipe is 'standard' RCP, while Class V would be the highest strength class for pipe before a custom pipe design is required.
 
You probably already considered this, but can you raise the profile for more cover?

"...students of traffic are beginning to realize the false economy of mechanically controlled traffic, and hand work by trained officers will again prevail." - Wm. Phelps Eno, ca. 1928

"I'm searching for the questions, so my answers will make sense." - Stephen Brust

 