gab1414
Structural
- Jul 9, 2012
- 2
I am looking at designing a concrete structure containing aqueous liquids to BS 8007: 1987. After analysis of the crack width of my retaining basement wall I find that I have a negative crack width. I spoke to a water engineer who advised me that this simply means that there will be no cracking in the concrete. The negative value arises as the average strain at the soffit of the beam (εm) is negative since it is equal the strain at the soffit of the beam (ε1) minus the strain due to stiffening of concrete between cracks (ε2). Since ε2 is greater the design surface crack width is negative. Does anyone know of a way to overcome this issue or even know a decent explanation as to why this occurs?