jlholt911969
Structural
- Sep 23, 2020
- 12
I have run into a problem that I have not had brought to me before. One of my projects has multiple 40x150 storage unit buildings with continuous slabs. Each slab has a step about midway. The slab is 4" thick with a thickened edge perimeter, and the step is 12" thick. I went out and inspected the first slab yesterday and it had a crack in it along the width of the slab about 18" from the step. The crack is about 1/2 the width of a dime or less. I just received an email that the owner has 5 more cracks in other parts of the slab that are all going across the 40' width of the slab. The project is in Minnesota near St. Cloud. There is rebar in the thickened part of the footing at the slab perimeter, and only fiber mesh was used in the slab part. All the soil compaction tests showed greater than 98% compaction. I am thinking that we are having temperature and shrinkage cracking, and I am wondering if it is because of the swing in temperatures between day and night. When I was there yesterday I did not see anything that would indicate the slab was covered at night, and night time temps have been in the mid-30s to mid-40s for the last 2 weeks. Daytime highs have been in the 50s to upper 60s. Control joints were cut at 12' on center in each direction. Where are the cracks coming from?