Description of the Issue:
In renovations carried out in the room of an existing building, a new ceiling bulkhead was constructed along the exterior wall. The bulkhead is framed with steel studs and clad side and soffit with drywall. The vertical depth of the bulkhead is about 2 feet, the length is about 70 feet, and the width of the bulkhead soffit is about 3 feet.
The construction was carried out about November of 2011. About February of 2013, several vertical cracks were observed in the vertical face of the bulkhead, and also in the soffit at the same location as in the vertical face.
The relative humidity in the heated / air conditioned room varies from about 25% in winter to about 60% in summer. The room is used for assembly purpposes for about an hour in the morning and an hour in the evening every day, and is empty the remainder of the time.
All the cracks occur where a re-entant corner is created in the vertical face of the bulkhead, by the old concrete beams that extend thru the vertical drywall.
The cracking is most probably caused by shrinkage of the drywall as the RH drops during the winter heating season, and the accompanying stress concentration caused by the penetration of the beam thru the vertical drywall. It is also possible that there is a drywall joint that has cracked open at these locations.
There would not be any structural settlement issue, because the building has been there for 50 years and has performed very well. There have been no structural changes. The 50 year old plaster walls in the building are uncracked and performing well.
Please see attached photos of cracks.
Questions:
1. What is the approximate expansion and contraction of drywall over the RH range that I oultined above?
2. How is that movement usually accounted for in the design?
3. Is it usual to put movement joints in drywall? If so, at what centres and how are they constructed?
4. What is the appropriate repair? Rout and patch and tape the cracks during the winter heating season when they are widest, or should movement joints also be installed at some appropriate centres?
4. There is also distress (looks like debonding of a corner piece) in the new drywall ceiling-to-new wall corner region (see photo). What is causing this? Is it a workmanship issue, or materials issue, or something else?
In renovations carried out in the room of an existing building, a new ceiling bulkhead was constructed along the exterior wall. The bulkhead is framed with steel studs and clad side and soffit with drywall. The vertical depth of the bulkhead is about 2 feet, the length is about 70 feet, and the width of the bulkhead soffit is about 3 feet.
The construction was carried out about November of 2011. About February of 2013, several vertical cracks were observed in the vertical face of the bulkhead, and also in the soffit at the same location as in the vertical face.
The relative humidity in the heated / air conditioned room varies from about 25% in winter to about 60% in summer. The room is used for assembly purpposes for about an hour in the morning and an hour in the evening every day, and is empty the remainder of the time.
All the cracks occur where a re-entant corner is created in the vertical face of the bulkhead, by the old concrete beams that extend thru the vertical drywall.
The cracking is most probably caused by shrinkage of the drywall as the RH drops during the winter heating season, and the accompanying stress concentration caused by the penetration of the beam thru the vertical drywall. It is also possible that there is a drywall joint that has cracked open at these locations.
There would not be any structural settlement issue, because the building has been there for 50 years and has performed very well. There have been no structural changes. The 50 year old plaster walls in the building are uncracked and performing well.
Please see attached photos of cracks.
Questions:
1. What is the approximate expansion and contraction of drywall over the RH range that I oultined above?
2. How is that movement usually accounted for in the design?
3. Is it usual to put movement joints in drywall? If so, at what centres and how are they constructed?
4. What is the appropriate repair? Rout and patch and tape the cracks during the winter heating season when they are widest, or should movement joints also be installed at some appropriate centres?
4. There is also distress (looks like debonding of a corner piece) in the new drywall ceiling-to-new wall corner region (see photo). What is causing this? Is it a workmanship issue, or materials issue, or something else?