I was called out to inspect a interior mezzanine in a retail stock room where there were cracks in the concrete deck. The owner wants to know if the cracks can be cosmetically repaired or the slab needs replaced. Upon looking at it, there were mapped pattern cracks all over. A few cracks had the reinforcement exposed and were missing the concrete along the cracks. A few other areas the reinforcement was visible at the top of the slab - likely a QC issue.
The spans are fairly short, varying 2' to 2'-6" between the bar joists below. The deck is 9/16 24ga conform and the net slab thickness is 1.5" with 6X6 W1.4XW1.4.
Fortunately, I had access the the original plans to confirm this along with field measurements.
Per the SDI Engineering manual, the concrete slab is the structural component. The manual makes this clear even though in the field there is bond between he deck and the slab. However, at 1.5" thick and poor QC I can understand why it cracked with bottom restraint at the deck and dynamic live loading from rolling carts, etc. It looks like it has been this way a while. Under ideal conditions the slab should have the capacity to support the 125PSF LL and the DL. Additionally, the form deck also has the capacity to support the DL & LL loads with L/240 (<1/8") defection with a SF of approximately 1.4 in the 2 or 3 span condition.
My engineer brain says that a structural system is damaged and needs to be replaced. I understand that all cracks aren't necessarily bad but the its the combination of poor qc, missing concrete, exposed reinforcement that makes me deem it unacceptable. I don't think grinding out WWM is going to be an option.
However, I wonder that since there is no "mathematical" threat of collapse, replacing the entire slab might be overkill for this application.
Any perspectives on how you would handle this are appreciated.
I am sort of stuck in this place of trying to communicate this to the client without a)creating a panic but also b)informing that a structural system has been damaged and should be repaired/replaced.
The spans are fairly short, varying 2' to 2'-6" between the bar joists below. The deck is 9/16 24ga conform and the net slab thickness is 1.5" with 6X6 W1.4XW1.4.
Fortunately, I had access the the original plans to confirm this along with field measurements.
Per the SDI Engineering manual, the concrete slab is the structural component. The manual makes this clear even though in the field there is bond between he deck and the slab. However, at 1.5" thick and poor QC I can understand why it cracked with bottom restraint at the deck and dynamic live loading from rolling carts, etc. It looks like it has been this way a while. Under ideal conditions the slab should have the capacity to support the 125PSF LL and the DL. Additionally, the form deck also has the capacity to support the DL & LL loads with L/240 (<1/8") defection with a SF of approximately 1.4 in the 2 or 3 span condition.
My engineer brain says that a structural system is damaged and needs to be replaced. I understand that all cracks aren't necessarily bad but the its the combination of poor qc, missing concrete, exposed reinforcement that makes me deem it unacceptable. I don't think grinding out WWM is going to be an option.
However, I wonder that since there is no "mathematical" threat of collapse, replacing the entire slab might be overkill for this application.
Any perspectives on how you would handle this are appreciated.
I am sort of stuck in this place of trying to communicate this to the client without a)creating a panic but also b)informing that a structural system has been damaged and should be repaired/replaced.