How would you create an artificial load on chilled water piping in order to perform a capacity verification on a chiller? The chiller is connected to an 8" piping loop, but with no air handlers or coils connected tied into it since it's been abandoned for some time. I imagine that there is perhaps a steam or hot water jacket that could be wrapped around a section of pipe to raise the temperature of water returning to the chiller. Does anyone have knowledge of such a thing or know where I could find more information? Other thoughts or ideas on adding load to a chilled water loop are welcome as well.
 
Replies continue below

Recommended for you

How do you plan to circulate the water in the loop with no air handler coils in place? Is there a bypass? If so, is the bypass near the chiller or out in the loop, away from the plant?

Has this chiller also sat a long time? How are its tubes in the condenser and cooler? Sitting a long time can foul them if the chiller was not drained prior to being mothballed.
 
Water will be circulated through a full size bypass in the loop, several floors away from the plant. The chiller has remained unused for about 2 years, but care was taken before it was abandoned. Chiller was drained down, refrigerant removed, and charged with nitrogen. The tubes will be inspected and cleaned prior to start up.
 
Add water to your loop at a known measured flow rate and temperature and let it drain after the chiller. Then measure the temperature of the draining water. A back-pressure regulator would be useful in the drain line.
 
I have some points:
- why do you want to check the chiller performance, do you want to bring it back to the service or the owner wants to sell it to someone else.
- your didn't mention your chiller capacity, but 8" piping loop and several floors, I guess your chiller is around 150 ton nominal capacity, how can you creat such load in a field test,
- if chiller is to be brought back to service, connect it to real load then check its performance, because if the chiller needs any care, you can do it later.
- if chiller is to be sold to another user then I thing a manufucturer or specialist contractor has to check it for liabilty.
 