I would like to know if there is a methot to determinate the kV of a cross bonding surge arrestor.
The standard method as used by NGTS in the UK is to select an arrester with a Ur of 1kV per 10kA RMS through fault current at the point of installation. So if the fault level is 40kA, then the rating of the CPA will be 4kV (Ur).
Does exist a more precise calculation? I can not fin it!
Thanks