I've been working through the design of a two-way slab based on the elastic frame method in the CSA A23.3 standard, and there is one part of the code that is unclear to me and I don't have the commentary or reference in terms of the rationale behind these provisions.
Based on my understanding, the standard provides two methods to establish the member stiffness - there is the non-prismatic modelling of member stiffness outlined in 13.8.2, and the prismatic modelling of member stiffness outlined in 13.8.3. The non-prismatic method seems to be the same methodology that's provided in ACI 318 for the equivalent frame method, so it's unclear why one would choose one method over the other given that ACI 318 does not have a second methodology to establish the member stiffness.
While digging a bit more into the theory behind these provisions, I also found this particular part of the PCA notes to ACI 318-11 interesting:
Reading that paragraph, it implies that the calculation of the equivalent column stiffness is only required for hand calculation methods like the moment distribution method. Does that mean that if you're using a frame analysis program, then it is not necessary to calculate the equivalent column stiffness and simply using the cross-sectional properties of the columns is sufficient?
Based on my understanding, the standard provides two methods to establish the member stiffness - there is the non-prismatic modelling of member stiffness outlined in 13.8.2, and the prismatic modelling of member stiffness outlined in 13.8.3. The non-prismatic method seems to be the same methodology that's provided in ACI 318 for the equivalent frame method, so it's unclear why one would choose one method over the other given that ACI 318 does not have a second methodology to establish the member stiffness.
While digging a bit more into the theory behind these provisions, I also found this particular part of the PCA notes to ACI 318-11 interesting:

Reading that paragraph, it implies that the calculation of the equivalent column stiffness is only required for hand calculation methods like the moment distribution method. Does that mean that if you're using a frame analysis program, then it is not necessary to calculate the equivalent column stiffness and simply using the cross-sectional properties of the columns is sufficient?