In diagram D17J, single-conductors are installed in a concrete duct bank. The phase conductors are in separate conduits. There is also a parallel set of phase conductors.
[ol 1]
[li]Since the phase conductors are in separate conduits, then which conduit is the bonding conductor supposed to be installed in?[/li]
[/ol]
I found some rules that seem relevant to this question:
[li] Rule 10-602
[/li]
[li] Rule 10-616 4)
[/li]
In these rules, it specifies that the bonding conductor should be installed with each group of parallel runs. However, it's not clear about how to install the bonding conductor if the group of phase conductors are in separate conduits.
[ol 1]
[li]Since the phase conductors are in separate conduits, then which conduit is the bonding conductor supposed to be installed in?[/li]
[/ol]