Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations pierreick on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

CSI front end characteristics question

Status
Not open for further replies.

MAGTiger

Electrical
Apr 30, 2008
107
Should it be considered normal for a CSI drive to draw significant triplen and even harmonics?
We are seeing as much as 14-18% even harmonic distortion and 10% 3rd harmonics. Total harmonic distortion is like 35%. The drive is running at about 50% of rated hp.

Neil
 
Replies continue below

Recommended for you

Even harmonics would suggest uneven firing of the SCRs (or other power electronics).
 
Is it safe to assume that this is current distortion, not voltage?
 
The voltage distortion is about 2-3%. There is s small amount of characteristic notching in the voltage wave.

Neil
 