veritas
Electrical
- Oct 30, 2003
- 467
An existing 3.3kV switchboard is to be replaced with a new one. There is a 400/1 existing CT with an EF setting of 20A (digital relay). The manufacturer of the new swbrd has replaced this CT with a 1000/1, Class 0.05PX200R5 (IEC 60044.1). An interposing CT is now required in order to achieve the 20A pickup as before.
I have two concerns here:
1) A 20A EF setting is now 2% of rated compared to 5% before. Is the requirement on the relay not more onerous now to detect a lower current signal amidst the surrounding noise (power station environment). Are spurious trips more likely? What about relay filtering? Relay used is SEPAM T20.
2) The increased CTR implies operating at a lower range of the CT mag curve. I have been told that the % error here is not covered by the IEC standard for Class PX CT's. In other words the standard specifies that at the top end (loosely speaking from about 2 to 3 times rated current to kneepoint voltage, Ek)the maximum mag current is 50mA.
However, at the lower range of the CT (below rated primary current)where I expect my EF operation to be as the maximum EF is only 500A, the %error is undefined. It is normally assumed that the CT is linear up to the Ek but there is no guarentee of this as accuracy and consequently errors are not tied down by the IEC spec.
Is this true?
Thanks in advance.
I have two concerns here:
1) A 20A EF setting is now 2% of rated compared to 5% before. Is the requirement on the relay not more onerous now to detect a lower current signal amidst the surrounding noise (power station environment). Are spurious trips more likely? What about relay filtering? Relay used is SEPAM T20.
2) The increased CTR implies operating at a lower range of the CT mag curve. I have been told that the % error here is not covered by the IEC standard for Class PX CT's. In other words the standard specifies that at the top end (loosely speaking from about 2 to 3 times rated current to kneepoint voltage, Ek)the maximum mag current is 50mA.
However, at the lower range of the CT (below rated primary current)where I expect my EF operation to be as the maximum EF is only 500A, the %error is undefined. It is normally assumed that the CT is linear up to the Ek but there is no guarentee of this as accuracy and consequently errors are not tied down by the IEC spec.
Is this true?
Thanks in advance.